Which conductor size is specified for the equipment grounding conductor of a 70-amp circuit?

Prepare for the ICC Residential Electrical Inspector Level 1 Exam. Study with our electrifying flashcards and multiple-choice questions. Dive into hints and explanations to boost your confidence. Elevate your knowledge and get ready to ace your exam with style!

Multiple Choice

Which conductor size is specified for the equipment grounding conductor of a 70-amp circuit?

Explanation:
The key idea is that the equipment grounding conductor (EGC) size is chosen from NEC Table 250.122 based on the rating of the overcurrent device. The EGC must be large enough to carry the fault current back to the source so the protective device can trip quickly, but it does not have to carry normal load current. For a circuit protected at 70 amps, the table specifies a minimum of 8 AWG copper for the equipment grounding conductor. That means an 8 AWG copper EGC satisfies the requirement, and is the smallest size that meets the code. Using 6 AWG or 4 AWG would also be acceptable (larger conductors are allowed), but 10 AWG would be undersized for a 70 A OCPD and would not meet the minimum.

The key idea is that the equipment grounding conductor (EGC) size is chosen from NEC Table 250.122 based on the rating of the overcurrent device. The EGC must be large enough to carry the fault current back to the source so the protective device can trip quickly, but it does not have to carry normal load current.

For a circuit protected at 70 amps, the table specifies a minimum of 8 AWG copper for the equipment grounding conductor. That means an 8 AWG copper EGC satisfies the requirement, and is the smallest size that meets the code. Using 6 AWG or 4 AWG would also be acceptable (larger conductors are allowed), but 10 AWG would be undersized for a 70 A OCPD and would not meet the minimum.